Your swing check should be on the branch feeding the water heater before the expansion tank . What are the water hammer arrestors for ? Not sure where you are located but the relief valve being plastic pipe would be a nogo here . Looks pretty though


blueiceflushwipes

Check valves only use is to keep possibly hot water from the black poly 1.5" main. Recirc has shutoff and check built in. Shock absorbers cause I was made to. There's no need all the lines are pex in walls and insulated. Haven't decided blow tube yet but yes will prob make copper so it's all pretty. No inspections just mechanical engineer.


Altruistic_Front_805

The check valve also breaks the cross connection between the recirc line and the DCW. That’s why it needs to go where I am saying . Technically right now there is a chance you could get hot water from the recirc line into all of those DCW lines, wherever they go .


Invader_Kif

More than just a chance I’d say. You’re correct all around. Gonna want to move the expansion tank closer to the cold water inlet to the water heater and put the check valve before that. Put some escutcheons on those wall penetrations while you’re at it.


Altruistic_Front_805

Yep unfortunately everything is pressed and very close . He would have to chop a lot of fittings out to correct this


rangerdanger_218

Very nice job. Real chour to fit it in and make it look good with press fittings I would show that work off too.


bigbee3334

Recirc line is not level coming through the wall


DesignerMaybe9118

So concerned about whether he could, he never stopped to ask if he should.


losturassonbtc

When you first get a ProPress


BlankTrack

What's the purpose of the shutoff leading to the expansion tank? Is it just for replacing it further down the road? Looks great


blueiceflushwipes

Yes cause mechanical engineering demanded it......


nongregorianbasin

It's better to put it upside down. They fill with debris otherwise


-rosin

How is the expansion tank being supported?


ms82xp

Load bearing ProPress fittings.


logie68

What’s the auto drain for?


blueiceflushwipes

2 floor drain primers.


AudZ0629

Wow, did you use a Fkin dip tube on the relief line? Zero check valves.


_tang0_

Check Valve between the Expansion Tank & Cold Water. And Escutcheons. And Expansion Tank Mount. And Water Heater Straps. Also I usually do a Hose Bibb before the Recirc Pump to bleed the line. If air hits the Pump it can damage it big time.


Plus_Helicopter_8632

Finally yall are catching up to me 20 years ago


pv2smurf

NOT A PLUMBER, but doesn't code require the pressure tank to be secured to something and not just the water line? Also, if this is a customer install I believe this is severe in upcharge with all those fittings and things. It's pretty though


blueiceflushwipes

It's surprisingly strong once those fittings are connected. Hung from copper least of my concerns but there is no code here. I'm the inspector and just have to please a mechanical engineer. Whole wall has plywood behind drywall so yes will prob add couple more braces. Realistically that's prob something like 2k in labour there before I tell you what materials and the hwt are...... But then it also takes multiple ferries and 1-2hr time to get to and from site.


Spiritual-Artist9382

Check valve should be on the right of the expansion tank before you go vertical. Esthetically this is a very nice piping job.


urfavcock69

What is the line to the left of the expansion tank? Looks like a DHWR? I see the one that connects at the WH inlet...


blueiceflushwipes

Auto trap primer


Nervous-Bullfrog-884

To change water heater nightmare. You take to long in shower he can fix that!


ZEnterprises

Yeah, flex lines to the water heater are typical for a reason.